Cooling Tower Upgrades

Cooling Tower Upgrades

Cooling Tower Upgrades

(OP)
I want to rebuild an old Lille-Hoffman cooling tower.  The original design was 100-85@78WB  The new conditions are 95-85@78WB.  I am in the Northeast,USA.  Are there contractors in the area that perform these services?  

How is the best way to guarantee performance when they are done with the project?

RE: Cooling Tower Upgrades

ENC, I'm bummed that you haven't got a respose yet, but I'm not a CT guru. Have you contacted Lillie-Hoffman people?

Your new criteria seem less restricive than the old (95-85@78 versus 100-85@78). Couldn't you use the same setup? Note that (always at the risk of sounding ignorant, not afraid to say it) I'm not sure what these values mean, although I'm pretty sure the 78 is a wet bulb temperature)... CB

RE: Cooling Tower Upgrades

ENC!

As your outlet temperature got reduced by 5 deg. F and inlet remains same you need not go for a revamp.The approach with your data seems to be 4 deg. C which is a little bit high. What type of a cooling tower it is?

1. FRP or Wooden
2. Honey Comb or Splash bar
3. For what application you are using it? (Range for cooling towers used for Generator radiator cooling is more)

Get the data viz., design approach, gas to liquid ratio and power consumption by fan from the repairer prior to the modification. Then check these parameters.

Generally 3 deg. C approach is good. Gas to liquid ratio is maintained anywhere between 1.5 to 2. (as per range)

Ask multiple values for inlet, outlet and design wetbulb temperatures to check range and approach to match various climate conditions.

Regards,

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources