Power flow control in low voltage networks
Dear members,
i am designing a system for a building which recieves its main supply from a wind turbine.
The building is still connected to the grid in order to provide a stable operation for the wind turbine (IG).
The utility however prevents injecting active power into the grid.
Other than regulating the active power produced by the wind turbine through pitch/yaw control or using dummy loads are there any available technologies in the market which regulates power transfer on low voltage grids?
Thank you
Thank you
RE: Power flow control in low voltage networks
"accumulate" the wind using a kind of water tower and fill it with a pump with the remaining unused power and use the water gravity potential
acting a turbine-generator as an alternative source when the wind is not available.
The pumped storage mechanism mentioned is one option as would be large battery bank that could be charged when there is excess power being generated.
What is the solution if this storage is full ?
any other ideas/innovations?!
Thank you.
I'm curious about the utility's refusal to allow export of power. Is this in the US?
I guess this applied to any distributed generation.
You could possibly do it by rectifing the incoming utility and wind generator onto a single DC bus feeding a large cap bank. Run the building via a large UPS powered by the DC bus and/or directly off the DC bus. Put a load dump on the DC bus that operates when the voltage reaches a certain threshold which is capable of absorbing the excess load from the wind generator. You could possibly use feed-back from this load dump to control the pitch/yaw of the wind generator.
Why does the utility not agree to backfeed? prc above gave the best answer: you cannot do it, the utility has to provide the stability and frequency regulation.
Unless it is a very small system (some few kW) all storage options are impractical and/or outrageously expensive.
rasevskii
There is a solution on the market for similar applications, though whether its applicable to your situation is another thing entirely.
I don't currently work for the company in the link, but it may be worth looking into.
Heating is a good choice. You can feed electric heaters with as much energy as is available and reduce your heating costs.
It has been suggested that feeding the DC bus of an inverter is a way to avoid back-feeds to the utility. You may consider driving the AC systems with VFDs and feed solar energy to the DC bus.
There may be times when you have excess energy.
Storage systems such as flywheels, pumped storage or batteries will be expensive to start with in smaller sizes and will be an excellent example of the law of diminishing returns as the size increases.
One use of storage may be to save excess energy in gusting conditions. The combination of demand on the solar system and overproduction of energy during high gusting winds make this a small window.
The cost per KWHr of a storage system will be very high.
My suggestion:
1st; Electric heating.
2nd; Feed the DC bus of VFDs.
3rd; Don't try to save energy for future use. If you must waste energy as part of your control scheme, boil water.
Bill
"Why not the best?"
Jimmy Carter