Cost Effective Interposing Relays / DC MCBs
Greetings
I need the manufacturers names who can provide cost effective Interposing Relays and DC MCBs for Switchgears. Both items shall be UL listed.
Big names offer high prices because of their names. I will appreciate your feedback.
RE: Cost Effective Interposing Relays / DC MCBs
What do you need from the interposing relay? Clifford & Snell's D series is first class, and although not 'cheap' per se I would say they are cost-effective. Areva's Prima range was also reasonable, although I'm not sure whether it went to Schneider or Alstom after the breakup of Areva.
rasevskii
As to your "smaller less expensive options", it is a poor criterion for an engineering decision. What you will find is that designing testing and manufacturing a proper DC rated relay is expensive. Then the economies of scale are not there to keep the cost low because they are not nearly as universally used as AC relays. So small companies are not going to be able to afford making "cheaper" versions because they will not sell enough of them to justify the considerable investment.
Just pick a good quality relay that fits your needs and negotiate as good a deal as you can up front, then move on. For something as low volume as Switchgear Control applications, you have likely already wasted more money that you can possibly save just by reading this post.
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
I've seen little octal-base plug-in relays used in this application that failed on the first trip.
Contacts welding closed is bad enough but contacts welding closed when trying to open may be worse.
Bottom line: be very careful interrupting DC current.
Bill
"Why not the best?"
Jimmy Carter
1- very fast , cannot break the DC current to an inductive load.
2- very slow , can break the DC current to an inductive load.