DP Flowmeter Terminology
DP Flowmeter Terminology
(OP)
Hello,
Could you please help me clarify the differences between the following terms:
- range?
- span? calibrated span?
- full scale?
- Max DP
Could you please help me clarify the differences between the following terms:
- range?
- span? calibrated span?
- full scale?
- Max DP
"We don't believe things because they are true, things are true because we believe them."





RE: DP Flowmeter Terminology
"Span" and "calibrated span" are the same as "range" and "calibrated range".
"Full scale" doesn't really have a meaning, it is often used as a synonym for "range", but sometimes it refers to the maximum value that an instrument can exhibit (for example the dP meter calibrated 0-100 inHg above might have the ability to be calibrated 0-1000 inHg).
"Max dP" is a nameplate value that is the largest calibrated range the instrument can have. Most pressure instruments have an uncertainty based on calibrated range. So if I have a 0-1000 inHg (nameplate) instrument that is +/-0.5% and I calibrate it to 0-1000 inHg then every reading is +/-5.0 inHg. If I take that same exact instrument and calibrate it to 0-100 inHg then every reading is +/-0.5 inHg.
David
RE: DP Flowmeter Terminology
You might first refer to the [link http:
metrology – Basic and general concepts and associated terms[/links] but you cannot be sure whoever is presenting you with these terms is using the same definitions.
There are also different conventions with different primary elements. Turbine meters are generally considered linear with flow and it is usual to quote accuracy as a % reading. The term calibrated span doesn't appear. Other flow meters are non-linear with flow. Variable area meters, for example, and it is more usual to talk of a %FS or percent full scale. With dP meters the situation is more complicated because while their is a square law relationship between pressure drop and flow, the same primary element (the orifice plate) can support multiple dP transmitters.
JMW
www.ViscoAnalyser.com
RE: DP Flowmeter Terminology
I've never seen an instrument (especially not a turbine meter) that the uncertainty was presented as a percent of reading. That would say at the very bottom of the flow range (where the meters are least effective) the "accuracy" of a +/-1% uncertainty device would be reported as something like 0.1 gpm +/- 0.001 gpm. At the top of the range (where the meters tend to be decent) the same meter might be 500 gpm +/- 5 gpm.
I've never bought an instrument that was that hard to pin down. The turbine meters that I've purchased came with a calibration certificate that showed uncertainty as a percent of calibrated range, and repeatability through multiple flow tests. The absolute value of uncertainty did not change from near zero to near 100% of flow.
David
RE: DP Flowmeter Terminology
Turbines have a linear range within which the "accuracy" (uncertainty) is a % of reading. They also usually show a minimum repeatable flow rate range. This is before we get into "smart" amplifiers which provide linearisation i.e. instead of a single meter factor will plot meter factor as against frequency.
VA meters, on the other hand, are commonly quoted as % FS. So 1% FS means that if full scale is 100l/min the error throughout the range is 1/l/min. At 10l/m you have a 10% error.
Higher accuracy versions may quote both a %fs and a % reading error to be used in combination.
Then again you have to beware of conventions. The convention for viscosity sensors is to quote % calibrated range. Since most have only a single calibrated range and a rudimentary calibration at that (because they usually operate as controllers with a single set point viscosity) there is no need for better. So the convention, when applied to more sophisticated sensors, rather obscures the true performance which is % reading.
There is a big difference between the two.
JMW
www.ViscoAnalyser.com
RE: DP Flowmeter Terminology
David
RE: DP Flowmeter Terminology
PD meters exhibit a similar characteristic curve. The "accuracy" or linearity declared is usually in the order of 0.25% of reading. Some get to 0.1% of reading. (The multi-piston meter is one of the most accurate of all PD meters, possibly of any meter).
Incidentally, the Cameron Turbines were originally designed by Milt November and manufactured by ITT Barton. These are a pretty good meter.
Vortex meters also quote a linear range and an "accuracy" of similar magnitude. The early Eastech Vortex meter was only claimed to be 1% of reading accurate but this was not simply a function of the linear range of the meter (the same meter factor over the meter range) but also a function of manufacturing tolerance as all vortex meters of the same size and duty had the same theoretical meter factor applied and they were simply tested to see if they came within the specification.
JMW
www.ViscoAnalyser.com
RE: DP Flowmeter Terminology
I've been seeing them recently on produced water dump lines and while they're pretty prone to sand cutting, if you can keep the sand out they've giving folks +/- 2-3% which in produced water is about an order of magnitude better than anyone else is doing.
David