chilled water pumps connection in the network.

chilled water pumps connection in the network.

chilled water pumps connection in the network.

(OP)
Dear all,

does any one help me. can we connect the primary, secondary & booster pumps in series before supplying the chiller.

please see the attachment in this file.

thanks,

RE: chilled water pumps connection in the network.

Why are you trying to turn a constant flow primary loop into a variable flow primary loop? Can your chillers even accomodate that much extra flow through them and still operate efficiently? My guess would be no without any other knowledge of the equipment.

Why not use a de-coupler loop between a constant flow primary loop and variable flow secondary loop to meet load?

RE: chilled water pumps connection in the network.

No, you've got it slightly wrong.  You need the decoupler mentioned above.  Google primary-secondary distribution.

 

 

RE: chilled water pumps connection in the network.

i admit some confusion, believing that some data is missing here.

why would you need pressure boosting linked with water supply network in first place?

this looks to me as water tower network of water cooled chillers, where series connections serves to overcome large pressure losses, possibly risers are very long.

system is created without decoupling and that can work, being adjusted properly - main pumps sense demand from chiller pumps and match their flow to chiller demand as they are VFD-driven, and all chiller loops contain solenoid on-off valves.

all of that would make sense to me if we talk about water tower loop. :)

RE: chilled water pumps connection in the network.

I agree that the decoupler is required.

The booster pumps look fine to me, they just maintain a maximum make-up water pressure to the system when the city water supply does not have the necessary pressure.

The issue is with the control and sequencing of the chiller staging and the flow from the VFD pumps.  The decoupler should help in that case.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources