Suggestions on how to account for the ehating load of a overhead door in a garage? (repair garage or municipal highway garage - door opens occasionally)

RE: Overhead Door Heat Load

Disclaimer: I do not have any experience with garage doors, but...

The rule of thumb I was told back when was to design for 10 cfm of OA per sf of door opening.  So this is the calculation I use for vestibules etc.  This oversizes the heating system near the door, but keeps the place when the doors are open for long periods of time.  You can makde it samller, but it will just be on longer to re-reach setpoint in my opinion.

 

knowledge is power

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources