ACI 350 or ACI 318?
ACI 350 or ACI 318?
Designing buried concrete vaults for a waste water commission that house various mechanical equipment. They are not fluid-retaining structures. Can anybody come up with an argument as to why one should design per the ACI 350? (Personally. I think it is overkill to do so)
"Structural engineering is the art of modelling materials we do not wholly understand into shapes we cannot..."...ah...screw it, we don't know what the heck we are doing.
RE: ACI 350 or ACI 318?
But this is why they pay you the big bucks. This definitely falls under engineering judgement. I can see a reasonable engineer arguing this either way.
Mike McCann
MMC Engineering
http://mmcengineering.tripod.com
If one approaches it from the IBC or ASCE definition of usage groups, it gets really sticky. The ASCE 7-05 seems like it could go either way as far as being low or high risk. It is a 54" valve (quite large!)on a line carrying potable water. Does this constitute a essential use building? If it fails, what are the consequences?
In the 'doomsday' situation, one could argue this is a critical structure and needs to remain in operation during crisis' for water access due to its size. Maybe analogous to the lack of redundancy of a 2-girder bridge. I agree that it could be the case for this structure. However, there is little or no probability of eminent failure, as earthquake loads are eliminated from load combination equations and the vault can be easily inspected via an access hatch.
frv, I am not so sure about exposure as it is above the groundwater table. Everything else equal, we don't use the ACI 350 for general retaining walls, e.g. landscaping structures, residential foundation walls, etc. Seems like other than the structure usage, exposure isn't a controlling factor alone.
To me it boils down to crack control for the longevity/durability of the buried structure, and not a hazard issue. I used ACI 318 for the initial design which resulted in As min equal to t&s steel in nearly every part of the vault. Without fail... changes were made at 70% submission, requiring a redesign. I am concerned that even with the lowest possible environmental factor from ACI 350, it will look like extra steel for 'no good reason'.
In the design review, the water commission didn't comment about the design methodology, so they obviously don't see a need or are as ignorant as I.
Also, be careful with your granular backfill. If the surrounding soil is not well drained, you will end up with a bathtub around your vault. We have that problem here (in Dallas.)