I am doing some R&D work by heating steel to 800C using high temperature cartridge heaters.  I am getting some earth leakage around 3mA at 230V AC at high temperatures causing RCD to trip out.

I am in discussion with cartridge heater manufacturer to improve performance of their heaters.

Would there be any safe way of stopping the tripping short of de-rating RCD to higher leakage current.

Measured leakage rises sharply around working temperature and falls when temperature is lowered. I assume insulation in heater is not up to the job.

Thanks

RE: Cartridge heater earth leakage at elevated temperature

A fall in resistance of Magnesium-oxide (MgO) is common at elevated temperatures. When using heat to dry the ends of mineral insulated cable The ends must be allowed to cool before a good megger reading will be obtained.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Cartridge heater earth leakage at elevated temperature

Since you have a high current closely associated with metal you can have inductive or capacitive leakage which would have nothing to do with "insulation" causing your leakage current.

Where's this 3mA you're measuring?

T'wer me I'd try to confirm this hypothesis as then you could come up with an appropriate solution.

Possibly run the heater with DC or use an isolation transformer.  Or assess the situation and use an RCD with a higher setting or dump the RDC altogether.  

Keith Cress
kcress - http://www.flaminsystems.com

RE: Cartridge heater earth leakage at elevated temperature

Measured leakage rises sharply around working temperature and falls when temperature is lowered.(800 deg. C)
Typical of MgO insulation.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Cartridge heater earth leakage at elevated temperature

I agree with waross as MgO resistance is low for an elevated temperature and I agree with itsmoked that  the cable capacity may add a few "mas" also. But my opinion is that a RCD [even of high sensivity] don't need to trip at 3 ma.[the usually rated is 30 ma and will trip instantaneously
at 20 ma].I think you have to check the RCD device. High sensivity RCD [in Europe, at least], is rated for 6,10 and 30 ma. There are RCD devices with variable sensitivity also.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources