4 20mA signal
4 20mA signal
Can I parallel a 4-20mA signal from a transmitter to a PLC input and another device such as a display?
Assuming both are compatible for a 4-20 signal
RE: 4 20mA signal
If you had a voltage input device you could convert the 4-20ma into a voltage by placing a 250 ohm resistor in series with the 4-20ma. The voltage drop across the resistor will be 1 to 5 Vdc. Quite a few devices actually work by first converting the 4-20ma into a voltage through the use of a dropping resistor.
RE: 4 20mA signal
RE: 4 20mA signal
RE: 4 20mA signal
My first thought was also the loop powered issue.
If they are not loop powered is series still the answer?
RE: 4 20mA signal
Most devices need at least 11vdc to operate. Don't forget in a series ckt the sum of the voltage drops is equal to the sorce. Increasing the supply voltage should take care of any problems.