Hello,
Consider a 4-unit non-stacked residential buildling (NFPA 13R). Each unit has its own exit. No common mechanical room. No fire alarm system is required.
I would like to install a valve pit.
Do you locate the flow switch and test & drain in the valve pit as well?
I appreciate any help.
Thanks.





RE: Valve Pit for 13R Project
RE: Valve Pit for 13R Project
Sounds like they need a dog house
And assume one feed for the entire building
RE: Valve Pit for 13R Project
RE: Valve Pit for 13R Project
cdafd:
Only one zone is required for the entire building since a fire alarm system is not needed.
It's a weird situation where this building does not have a common mechanical room and needs a double check valve assembly (as opposed to dual check valves and the reason for the valve pit).
Regarding the FDC, I would locate on the front of the building and connect to the nearest point of the largest main inside. Probably a 2 1/2" FDC with a reducer to 1.5" to match main.
RE: Valve Pit for 13R Project
What part of the country is this???
RE: Valve Pit for 13R Project
Just so I'm clear, a small dog house is a closet sized addition to the house that is heated and accessible with key from outside the building by all tenants?
This project is in the Pacific Northwest.
RE: Valve Pit for 13R Project
RE: Valve Pit for 13R Project
This project is in the Pacific Northwest.
yes with heat and light big enough to work in and you can have the backflow and fdc there
is this a townhouse or what is it???
RE: Valve Pit for 13R Project
It's a four unit, 3-storey, non-stacked residential building.