I have a 1.5 hp 115/230v pump that draws 22/11 amps. The type of controller I want to use for the application only handles 10 amps. Is there a way to still use this controller? What if the controller is only a 15amp-110v controller?
http://store.waterpumpsupply.com/60gpm15hp11v.html
http:/ /lib.store .yahoo.net /lib/kingp umps/LEA-C TL-Gray-Hy drotronic- Manual.pdf
Where would I look online to find products suggested?
http://store.waterpumpsupply.com/60gpm15hp11v.html
http:/
Where would I look online to find products suggested?





RE: Could I use a relay/resistor for this
This assumes that it's a simple Off/On control system.
A careful system designer would also consider the implications of the decreased MTBF due to the added complexity.
RE: Could I use a relay/resistor for this
11 Amps on a 10 Amp controller? Not good.
22 Amps on a 15 Amp controller? Even worse.
1.5HP motor? Use an HP rated switch. Look at Square D 9013 series HP rated switches.