Hi,
I need some suggestion about how to start 200kW ventilator (400/690V 2 pol or 4 pol)?
I have two ventilators. Ventilator 1 is 200kW and for continuously, when ventilator 1 goes down(defect), ventilator 2 has to start automatically. What is best solution for start so big fans and how to switch automatically if the fan 1 defect.
Switche has to be quickly as possible.
thank you!
I need some suggestion about how to start 200kW ventilator (400/690V 2 pol or 4 pol)?
I have two ventilators. Ventilator 1 is 200kW and for continuously, when ventilator 1 goes down(defect), ventilator 2 has to start automatically. What is best solution for start so big fans and how to switch automatically if the fan 1 defect.
Switche has to be quickly as possible.
thank you!





RE: 200kW ventilator-start
If the power source is enought I will start each one DOL.Then
You could install air sensors(Air pressure) in each duct of each ventilator(Fan) to detect if is or not in operation in order to command the backup fan starting. Also you can analize the option of use VFD to obtain energy savings, in this case you can connect the contacts and signals from one VFD1 to give advise to the other VFD2 to operate in case of failure or accidental disconnection.
Regards
Carlos
RE: 200kW ventilator-start
Keith Cress
kcress - http://www.flaminsystems.com
RE: 200kW ventilator-start
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 200kW ventilator-start
Soft starter, star-delta or frequency inverter?
RE: 200kW ventilator-start
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: 200kW ventilator-start
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: 200kW ventilator-start
Keith Cress
kcress - http://www.flaminsystems.com
RE: 200kW ventilator-start
I don't look time as time. It has to be safety when changeover is made. Fan 1 has to stop and then fan 2 start. If is that 10 min it will be 10min if 30min it will be 30min.
I look for VFD from Danfoss FC302.
RE: 200kW ventilator-start
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: 200kW ventilator-start