How would you start this investigation?
There was a partial collapse of a parking garage near Penn State on September 4th.
Part of the structure was a slab on grade with a retaining wall. That portion is still in place. The other part was framed as follows:
- asphalt topping on
concrete-topping on
DOX plank floor system (essentially, a panelized prefabricated
assembly of concrete block with rebar grouted into voids near the tension face of the panel) framing between lines of steel girders, both cantilevered and drop-in spans, over
steel columns
masonry shear walls at the perimeter
RE: How would you start this investigation?
After the typical initial steps of background, construction, age, exposure, etc. the most obvious approach would be to investigate corrosion...rebar and connections.
Structural overload is rarely an issue with parking garages that have been in place for a while. Deterioration of members/components/connections would be the center of my attention, considering the time of year,lack of wind loading (unless you had a coincident storm event!), etc.
Ron
I have recently begun my own investigation on an existing one story building. I believe the roof structure is DOX Plank. I am in search for material specifications and detail information on DOX Plank. Do you have any further information on this building system? Or know of a particular direction to take?
Jessica
As with any investigation I would start by checking with people in the area. (ie. security guards or locals) as to the weather and if they had witnessed or heard anything at the time. For example this may lead to clues such as heavy rain resulting in large hydrostatic pressures from old, broken storm water lines.
I have found this initial approach helps greatly with respect to starting my calculations.
VOD
Thanks in advance,
Mozzo
DOX plank was probably the first precast-prestressed plank manufactured in the (us).It appeared around the 1950's.
the planks were 16" wide,and were mostly 8"in depth.
It was a decent prefab concrete material(used in motels,and other reprtitive structures where cmu walls and steel framing occured.the biggest problem with it was the steel.
At that time steel was not at the proper or max strength yet.
this makes the product suitable only as a mild reinfoced product.Rich2001,when you get to the Dox part of your investigation look hard at the steel and pressure tha the design engineers intended for the deck.
I have a similar problem with a 1950s structure.
Don't know any other way to consult with you except this reply.
Please talk to me within the guidelines of eng-tips.