long span joist welded at both ends
long span joist welded at both ends
(OP)
Consider a single story precast building with 60'LH joists. Would there be any issues if the joist is welded at both ends rather then welded @ one and bolted at other? i.e any thermal movement issues?
Personally I think there shouldn't be any problem because the wall panels are precast with regular and more efficient (as opposed to cmu) control joints plus the pre-engineered camber should some how help too, but I am not sure.
FYI-building dim: 60x100.
Personally I think there shouldn't be any problem because the wall panels are precast with regular and more efficient (as opposed to cmu) control joints plus the pre-engineered camber should some how help too, but I am not sure.
FYI-building dim: 60x100.






RE: long span joist welded at both ends
I am currently designing a building that is 125'x125' clear span with the joists welded on each end (actually each end is both welded and bolted because OSHA requires joists over 40' to be bolted). If you run into any issues let me know.
RE: long span joist welded at both ends
I have come up with less then 1/2" of change in length over a 180 (+/-90) degree range for the 60' span. So certainly doesn't seem like it should be an issue.
RE: long span joist welded at both ends
RE: long span joist welded at both ends
RE: long span joist welded at both ends
Check out this paper, hopefully the link will work.
http://www.nap.edu/openbook.php?record_id=9801
At the end of the paper they give temperature changes for various cities in the US.
RE: long span joist welded at both ends
But near the corners, the walls can't rotate as easy due to the intersecting concrete wall that is parallel to the joist.
I agree that the thermal loads aren't that much but they are a sort of irresistable force. If the thermal deflection is 3/16" to 1/4" then that might be the crack width you see at the seat at one end.
RE: long span joist welded at both ends
@ JAE: Thank you for the informative post. I am just wondering how a detail would look like over a precast wall? Would you use 2 headed studs in the precast angle that the joists seat can sit on?
RE: long span joist welded at both ends
Good lord! If you though about the axial load developed to represent a 1/2" change of length if fully restrained, you wouldn't be making such a statement. Of course, in all likelihood, that kind of restraint would only happen near building corners as pointed out by JAE, and the joist will bow and relieve some of the stresses... but to make such a statement is not to recognize the tremendous forces that can be developed due to thermal.
RE: long span joist welded at both ends
I would think joists would probably bow or buckle a bit given their light I or mass!!
RE: long span joist welded at both ends
The paper I referenced give a delta T of 61 degrees for St Louis. I understand the temperature swings that can happen in a give region however, you have to realize that you are not going to weld the joists to the support structure on the -15F day and expect the job to still be exposed to the elements on the 108F day... well maybe for a very large project.
RE: long span joist welded at both ends
While I cannot disagree with your argument - this one beam was installed in the dead of winter - say at 10F. Then at 100 F it "blew" out later in the summer!!
True story!! and well documented!!
Go work in Fort McMurray Canada or Minneapolis, MN ---- You will be AMAZED by what can happen!!