Punching shear in beam
(OP)
Can punching shear be a problem in beam if the flexural shear capacity is satisfied? (ie. providing beam ligatures)
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Punching shear in beam
Yes, if the beam is wide enough compared to the support width for there to be a critical shear plane transverse to the beam direction.
This must be checked for Band beams which are normally wide and shallow.
RE: Punching shear in beam
If punching shear has to be checked, would you treat it as punching shear in a flat plate? Would you consider the effect of flexural shear reinforcement in the check? If yes, how does the code include the shear reinforcement?
RE: Punching shear in beam
If the reactions from the beam grillage are high enough to cause a punching shear problem then you would be better of with a pile cap.
RE: Punching shear in beam
Yes, the check would be the same as for a Flat Plate or a Flat Slab but based on the overall depth.
If punching reinforcement is needed, I would think you could include the flexural shear reinforcement on the faces where it is required for the extent of the punching perimeter in your calculation of the area of punching reinforcement to add. Your flexural shear reinforcement will be full width of the beam but you should only consider that which is in the punching zone.
Another solution, if the concrete shape is not fixed, would be to add a Drop panel to the soffit of the beam at the support (as you would do for a Flat Slab but only for the width of the beam, not L/3). This would have several effects for you, reducing flexural reinforcement, increasing flexural and punching shear capacity and reducing deflections. THis would be preferrable as detailing punching shear reinforcement will not be easy.