induction motor

induction motor

induction motor

(OP)
Hello, If there is unstable line to ground voltage on a delta connected three phase induction motor motor what effect can it have on the motor. Given the line current and the line to line voltages are stable and within specification.
please advise.
 

RE: induction motor

If the line-ground voltage is less than the line-line voltage it probably has no affect.  

RE: induction motor

I second David Beach's comment.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: induction motor

It could be a weakened insulation somewhere-in the motor or in supply side [upstream].But I agree with the conclusion for the time beeing it is no change in motor behaviour  
 

RE: induction motor

Hello all,

If the system is 3-Ph 4 Wire (i.e. Star connected, neutral grounded transformer), the voltage on any phase to ground will rise only in case one of the other two phases develops a low impedance earth leakage due to insulation failure.

In this case, there seems to be one. However, if it is well below the protection settings of the upstream switchgear (Sensitive E/F), there is no reason for immediate worry. But, it would be a good idea to get the IR's for the system rechecked.

Hope the answer is acceptable. Please correct me if I am wrong.

Fahad Shaikh.  

RE: induction motor

Please correct me if I am wrong.
Any fault capable of noticeably changing the voltage to ground on a grounded system will will be cleared by the protection before the voltage difference is apparent.  

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: induction motor

You are right, waross,usually the insulation degradation is so deep that the current to ground turns into short-circuit activating the protection.
But in this case-4 wires distribution- could be a current unbalance and the neutral current circulation deploys the neutral point- in a remote location
from the grounded transformer neutral.So, nothing is concerning about ,indeed.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources