Heat exchanger high delta p
(OP)
This is a problem with heat exhanger unit. It is a multi tube type heat exchanger. I was told by the operator when he opens the bypass valve the pump feeding discharge to the heat exchanger drops 20#. There are two bag filters upstream of the heat exchanger. First I thought filters might need to get changed but the operator gets high delta P throgh the heat exchanger.
Any thought what the problem might be?
Any thought what the problem might be?





RE: Heat exchanger high delta p
If it is abnormal, my first guess would be filterable solids have somehow by-passed the filter and plugged some of the tubes. Second guess, fouling.
Good luck,
Latexman
RE: Heat exchanger high delta p
Maybe in the first place the configuration of the baffles or the TEMA type really gives high delta P.
RE: Heat exchanger high delta p
Everything sounds perfectly normal to me. You are bypassing something - you didn't stipulate whether the Hx was bypassed or the filters, however, I suspect it is the Hx. Regardless, something in the pump discharge flow stream with a pressure drop was bypassed and the pump had less "system" resistance and ran out out to the right on its curve.
Want to make a bet? I'll bet that your pump's motor amps jump up too when he opens the bypass. Try it.
All sounds well as I see it.
rmw