From Generator to ATS through Seperate Feeders

From Generator to ATS through Seperate Feeders

From Generator to ATS through Seperate Feeders

(OP)
We have a ATS at our remote site rated 500A.Now we want to give Generator power from Main Site to ATS at Remote site.

There are two Generators in Parallel at Main Site.Each Generator
has a spare feeder of 250A.

How we can connect these two 250A feeders to one Feeder so that
a 500A ats can be served.

I hope you understand my question.

regards

Abraham  

RE: From Generator to ATS through Seperate Feeders

You can't.  At least not if the NEC is your governing code.

RE: From Generator to ATS through Seperate Feeders

Can you show us a diagram? Your description is quite vague.
But, as David says, probably not.
You may be able to reuse the feeders after rewiring/reconnecting them.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: From Generator to ATS through Seperate Feeders

Consider removing the paralleling bus and designating the bus where the sync check is connected as the paralleling bus.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: From Generator to ATS through Seperate Feeders

Hi man,
There is something wrong in your drawing (or something i don't get well...)

I assume that CB of 630Amps shown bellow each generator is the main CB of each generator.
Is this is true, then is not possible to have a parallel bus before generators circuit breakers!
As soon as you start the Generator will supply power to the "paralleling bus" no matter if the respectively 630Amps is open or closed and this is something you don't want.

As "waross" proposes, remove completely the parallel bus bellow generators and everything should work fine.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources