Retaining Wall Cracking Between Joints

Retaining Wall Cracking Between Joints

Retaining Wall Cracking Between Joints

(OP)
Hello.  We've been asked by a client to comment/advise on a short (3'-5' tall) reinforced concrete retaining wall that has been constructed and is showing cracking at locations between expansion/contraction joints provided at roughly 20' oc.  The client suspects that the contractor did not discontinue the rebar at the joints or provide a slip on one end.  Vertical cracking is showing exclusively at weep hole locations, full height.  The wall is an aesthetic feature, and efforts to patch the crack with injected epoxy and thin mortar layer have not been successful - the cracks return. What would be the risk in cutting the rebar at the joints at this point?  Would that relieve the stress such that a patch of the existing cracks would stay closed? Other ideas? Thank you!   

RE: Retaining Wall Cracking Between Joints

If you cut through the wall at the expansion joints nothing will happen to the wall.

If the contractor did in fact discontinue the bars it could be that your joint spacing is too large for a low rise wall.

RE: Retaining Wall Cracking Between Joints

Since this is at weep hole loctions, I would also consider freeze-thaw action in the area of the weep hole that it could be encouraging the vertical cracking.

I do think that the horizintal rebar scenario is the most likely though as previously mentioned.  With this though, if the bars are at the center of the wall, the cut will have to be in the order of half the wall thickness.  

The epoxy injection into the cracks will not work.  It is too rigid.  You need a flexible sealant - something that will move but remain sealed and bonded with a variation in temperature.

Mike McCann
MMC Engineering
http://mmcengineering.tripod.com
 

RE: Retaining Wall Cracking Between Joints

Concrete walls restrained by previously placed footings or slabs will invariably crack at about 10 to 12 ft spacings.  More reinforcement will control the cracking, but nothing will completely prevent it.  The cracking will be much more noticeable in low walls as in this case.

RE: Retaining Wall Cracking Between Joints

hokie66 is correct.  It would be good if you could post a few photos.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources