I have a question about maximum cable length between VFD and motor ,MV or LV , is there any table or formula in this regard?

RE: VFD CABLE

No table that would be meaningful as a generalization across platforms. Different drive topologies will cause different problems and dictate different strategies to deal with them, which will always affect the maximum length of motor lead cable. The type of cable makes a difference as well. If you have a specific issue and you know the details of what you have to deal with, post it and there are many people here that can offer strategies.

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: VFD CABLE

I'm sure jraef's comments are on the money.

Google "Riding The Reflected Wave" for one article on the subject

=====================================
(2B)+(2B)'  ?

RE: VFD CABLE

RE: VFD CABLE

On the other hand ABB sustain that their driver provided with dv/dt filter will present no overshoot at any frequency-no limitation for 600 V cable.
That means the usual criteria of load and short-circuit heating and voltage drop will rule the supply cable choice.
See:
http://www.google.co.il/url?sa=t&rct=j&q=technical%20guide%20no%20102&source=web&cd=1&;sqi=2&;ved=0CDEQFjAA&url=http%3A%2F%2Fwww05.abb.com%2Fglobal%2Fscot%2Fscot239.nsf%2Fveritydisplay%2Ffec1a7b62d273351c12571b60056a0fd%2F%24file%2Fvoltstress.pdf&ei=zUlnT8X8NKm00QWHx-TACA&usg=AFQjCNG62eYYBqdiwGs_f1GsHT_NO5Nkjg
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources