L.S.,
I would like to check a certain feature with others about copntrolling a level in a horizontal cylindrical tank. I have been taught that for level control it is wise to have a certain dead zone around the nominally desired level, so that small deviations will not immediately require controlling action and that the tank will function more like a volume buffer.
Are there any considerations pro or against to actually stick to this rule?
Thanking you in advance for your comment I remain
with best regards,
Karel Postulart
I would like to check a certain feature with others about copntrolling a level in a horizontal cylindrical tank. I have been taught that for level control it is wise to have a certain dead zone around the nominally desired level, so that small deviations will not immediately require controlling action and that the tank will function more like a volume buffer.
Are there any considerations pro or against to actually stick to this rule?
Thanking you in advance for your comment I remain
with best regards,
Karel Postulart
Karel Postulart, The Netherlands
Nuon Power Generation





RE: Level control in a horizontal cylindrical tank
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.
RE: Level control in a horizontal cylindrical tank
RE: Level control in a horizontal cylindrical tank
Thank you for your swift response and helpfull information.
With best regards,
Karel Postulart, The Netherlands
Nuon Power Generation
RE: Level control in a horizontal cylindrical tank
"It depends..."
As an example of a dead band, we had a condensate return tank where the dead band was between about 15% and 20% of tank capacity. When the condensate return flow surged, the tank would go to almost 100%.
The normal operating level was between 20% and 90%. If the level went below 15% it was topped up to 20%. Not all of the steam was returned as condensate. From time to time, generally due to operator error, the level would go to 100% and excess water would overflow and be wasted.
Bill
--------------------