Heat Transfer thorugh Cable Insulation from a single source
hildeew2 (Electrical)
15 Mar 12 11:09
Hey all,
I am trying to determine the heat flow into the insulation of an electrical cable with insulation from a heat source touching it at one point along its length. (Like a cylinder sitting on a hot slab) I am ignoring any convection at the moment.
I have the equation:
Q = (2pi*k*l*(T1-T2))/(ln(r1/r2))
But i believe this is for a temperature source surrounding the entire circumference and not just at a point.
Please let me know if I am wrong about the equation and if not what equation i can use to solve for the heat flow into the cable insulation.
Thanks.
vpl (Nuclear)
15 Mar 12 12:13
Is this a school assignment?
Patricia Lougheed
Please see FAQ731-376: Eng-Tips.com Forum Policies: Eng-Tips.com Forum Policies for tips on how to make the best use of the Eng-Tips Forums.
15 Mar 12 12:59
No.
It's a calculation to support the experimentally proven fact that conductors running single phased in metallic conduit will melt the insulation.
I left this out to try and keep my question simple as to not create a side discussion about the experiment itself, which will surely now happen.
Thanks for your input.
MintJulep (Mechanical)
16 Mar 12 16:51
The simple one-dimensional equation you have is not going to get you where you need to be.
You would appear to have at least two-dimensional heat transfer, with internal heat generation.
Probably not safe to ignore convection either.
Start with a clear statement of the problem.