s it a Nonstructural Component or Non building Structure?
Hi all,
wondering what you would categorize the attached air filter dwg.  Is it a
A.) Nonstructural Component (ASCE 7-05 chapter 13)
or
B.) Non building Structure  (ASCE 7-05 chapter 15)
I'm leaning towards B, even though it is, technically, a mechanical unit.  But, since this air handler is not attached to a main laterally resisting structure and is a stand-alone structure (i.e it's gotta resist the lateral loads on its own.  I feel it would fall under chapter 15, table 15.4-2, under elevated tanks, vessels, bins, hoppers (ASCE 7-05).
I've also noticed that the seismic load for this air filter corresponding to category B is almost 40% greater than that of A.
RE: s it a Nonstructural Component or Non building Structure?
I agree with Mike.
I have some experience with mechanical units where I used Chapter 15 for the same reason as you.
By going the more conservative route you also avoid any complications that could arise if the plan checker doesn't agree with a chapter 13 justification attempt.
PMR06
great article,  thanks for the reference..