Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...I just wanted to say THANKS for the forum. The knowledge I gain from your site is invaluable..."

Geography

Where in the world do Eng-Tips members come from?
Tankie (Structural)
14 Mar 12 12:02
I don't want to derail the recent thread about the Section 12.5.3 modification factors for footing dowels, so pardon the semi-parallel subject.

The specific case that has me a bit confused is when a hooked bar (hairpin) is used to provide the needed Appendix D reinforcement for anchors in tension.  The elevation view of Figure RD.5.2.9 in 318-11 illustrates this case perfectly.

The question that I have is as follows:  Can the "excess reinforcement" provision of Section 12.5.3(d) be applied to this hooked anchor reinforcement in order to reduce the standard hook development length ldh?

I'm thinking that it CANNOT be used, since 12.5.3(d) states that this knockdown factor can only be used when "development for fy is not specifically required", and the Appendix D provisions, I believe, would require the anchor reinforcement to be designed based on yield.

Would appreciate your thoughts.

Thanks.
Helpful Member!  jdgengineer (Structural)
14 Mar 12 12:31
I think this is an area that requires judgement. I'd say that I tend to agree with you, that it isn't wise to reduce the development length of reinforcement that is there to preclude the failure of a concrete breakout mechanism.  However, in my opinion it may be acceptable by the code given some conditions.

A ductile failure of the anchor in Appendix D is not required, but it's encouraged.  Per Section D3.3.6 you are allowed to take the design strength as 0.4 times the design strength as determined in D3.3.3 if the anchor is governed by a concrete failure mode.  I would think that if you were to design for a reduced development length this failure mechanism would now be considered a "concrete failure mode" as the failure will be bar slip in the concrete.  Therefore, in my opinion if you take 0.4 x design strength and calculated your development length based on this reduction it satisfies the intent of the code.

The language in D.5.2.9 states only that the anchor is developed in accordance with Chapter 12, therefore, in my opinion, the reduced development lengths are technically allowed.

However, I doubt you'd be reducing your development length much with this reduction in place, and I don't think except in some odd situation that I would ever pursue it.
Tankie (Structural)
15 Mar 12 18:15
Thanks, jdgengineer.  I agree, even if permitted by ACI there isn't much bang for the buck to be realized.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close