Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

LINK TO THIS FORUM!

Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Feedback

"...This is a very good site. Please keep it running. Thanks and wishing a great health and success for the site and its owners..."

Geography

Where in the world do Eng-Tips members come from?
prc (Electrical)
10 Mar 12 6:13
I find the following terms when referring to a turbogenerator(400MVA)data sheet.

1) Direct axis synchronous reactance

2) Direct axis transient reactance

3) Direct axis  subtransient reactance

4) Quadrature axis synchronous reactance

5) Quadrature axis transient reactance

6) Quadrature axis subtransient reactance.

Hope the percentage reactances mentiond should be with respect to the rated full load rating, at  rated  lagging power factor and maximum hydrogen temperature.

Can the experts  briefly say what it is,significance for operation,which ones come in to effect during short circuit, normal operation and load sharing (if loading to a common bus.
Helpful Member!  7anoter4 (Electrical)
10 Mar 12 10:06
I'm not pretending to be an "expert" in Electrical Power System Analysis.
So, simplifying the basic equations I think we may say the following:
Ik=U/Xd Permanent short-circuit current[ss c]
I'k=U/X'd Transitory  ssc
I"k=U/X"d Supertransitory  ssc
Where:
U=Generator terminal voltage
delta=load angle [between Eo and U]
Eo=no-load emf
E'do=transitory emf
Pa=Eo*U/Xd*sin(delta)+U^2/2*(Xd-Xq)/(Xd*Xq) Stationary regime active power.
P"a=E'do*U/X'd*sin(delta)+U^2/2*(X'd-Xq)/(X'd*Xq) Transitory regime active power
A  phasor diagram may be more explicating
 
7anoter4 (Electrical)
10 Mar 12 10:55
I forgot the phase-to-ground short-circuit.
For phase-to-ground short-circuit we need Z2. X2=(X"d+X"q)/2
 
Skogsgurra (Electrical)
10 Mar 12 10:58
Would that mean that "Direct" means resistive and "Quadrature" neans reactive (90 degrees)?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

Helpful Member!  Hoxton (Electrical)
10 Mar 12 12:52
Would that mean that "Direct" means resistive and "Quadrature" means reactive (90 degrees)?  - yes

I usually explain all this to my mechanical engineer colleagues by saying that reactances do not exist.....  If you put a short circuit across the terminals of a generator, the current will rapidly increase and then gradually decrease.

To use this in calculations you have to imagine a generator with a voltage source and a variable reactance.

When operating normally, the reactance is large (synchronous)

When the fault is applied, it is very small (subtransient)

And the then rises (transient)

As regards the direct and quadrature components, if you look at a salient pole generator (like fitted to a 500kVA standby diesel).  The magnetic path between the rotor pole face and the stator is easier (only interupeted by the air gaps) than if you took the path between the poles where the air gap is large. Basically that explains the difference.

The reactances are usually referred to the rated VA of the generator.

 
7anoter4 (Electrical)
10 Mar 12 12:54
The Salient Poles Synchronous Generator Rotor [inductor] magnetic field is deformed by stator [induced] reaction field.
Mathematically we can decompose this field in 2 sinusoidal magnetic fields produced by stator one acting in the pole and another  
between poles. The reactance produced by these fields will be xad [direct armature reactance in pole axis ]  
and xaq [Quadrature axis armature reactance]
The stator magnetic field losses produces a loss reactance Xs. The direct axis synchronous reactance then will be Xd=Xs+Xad
and  Quadrature axis synchronous reactance will be Xq=Xs+Xaq
As we know the pole is provided with excitation winding and [usually] oscillation damping [I don't know if my translation is correct name]
winding and in a short-circuit case these fields will produce an other change in synchronous reactance and we'll get X'd and X"d [respectively X'q and X"q]
 
dpc (Electrical)
10 Mar 12 14:55
http://en.wikipedia.org/wiki/Dqo_transformation

Some info on Park's (or Dq0) transformation.   
prc (Electrical)
11 Mar 12 0:44
Thank you gentlemen.Then what is the significance of following:

1) Stator Leakage Reactance

2) Zero sequence reactance

3) Negative Sequence Reactance
7anoter4 (Electrical)
11 Mar 12 13:52
First of all I'm sorry I didn't notice the first sentence of the o.p.:
"I find the following terms when referring to a turbogenerator(400MVA)data sheet."
So, as a turbogenerator has a cylindrical [not a salient pole] rotor and Xd=Xq.
Second, I translated wrong instead of  "field leakage reactance " into "field losses reactance" so what I noted Xs it is actually Xla [armature-stator-leakage reactance].
I have to apologize for my bad English!
Stator leakage field is "a lost field" indeed, since it does not flow with the main flux but it remains in the air space as slot and open winding ends. This includes also the magnetic field harmonics[ as differential leakage].
The negative and zero sequence reactance are used in the connection with short-circuit case as in steady state balanced regime the generator only generate
positive sequence voltage and negative and zero sequence voltages are zero.
Nevertheless, negative sequence currents can arise whenever there is
any unbalance present in the system. Their effect is to
set up a field rotating in the opposite direction to the
main field generated by the rotor winding, so subjecting
the rotor to double frequency flux pulsations. This gives
rise to parasitic currents and heating.
If a machine is operating with an earthed neutral, a
system earth fault will give rise to zero sequence
currents in the machine. This reactance represents the
machine's contribution to the total impedance offered to
these currents. In practice it is generally low and often
outweighed by other impedances present in the circuit.
 If Y point is grounded through impedance  Zg  , then  3*Zg
 will have to be added to zero sequence impedance of generator.
 

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close