water tanks-net capacity

water tanks-net capacity

water tanks-net capacity

(OP)
I am sorry for this rookie question, but I can not find where the norm NFPA stablishes how to calculate the volume that the water tank for private fire protection should have.

I only found the "standard net capacity sizes" on the NFPA22, but I didn´t find any tips on how to determine the size.

Can anyone please help me to find it?

RE: water tanks-net capacity

NFPA 13 is where the details are located.

Sprinkler demand + inside hose streams + outside hydrants times the duration based on the occupancy. Light 30 min, Ordinary Haz 1 & 2 60 mins, Extra Haz 1 & 2 120 mins. Warehouses 120 mins, ESFR 60 mins.

Example

Light hazard .10/1500= 150 gpm plus 100 gpm hose = 250 gpm times 30 mins = 7,500 gallons. If no inside hose then deduct 100 gpm.

Hope this helps.

****************************************
Fire Sprinklers Save Firefighters' Lives Too!


 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources