It will operate off discharge air temperature with room temperature ov
It will operate off discharge air temperature with room temperature ov
(OP)
Hi,
I was reading an HVAC tech sheet and confused by some sentenses in the sheet:
The heating on this unit will be run off discharge air temperature with room temperature override.
It will operate off discharge air temperature with room temperature override.
I guess these two sentenses mean that the new temperature will not be restricted by the discharge air temperature setting and the room temperature will be changed due to this.
Could anyone help me understand what is the meaning?
Thanks so much!
I was reading an HVAC tech sheet and confused by some sentenses in the sheet:
The heating on this unit will be run off discharge air temperature with room temperature override.
It will operate off discharge air temperature with room temperature override.
I guess these two sentenses mean that the new temperature will not be restricted by the discharge air temperature setting and the room temperature will be changed due to this.
Could anyone help me understand what is the meaning?
Thanks so much!





RE: It will operate off discharge air temperature with room temperature ov
The control first tries to maintain a set discharge temperature.
However, if the room temperature is too far below the room setpoint then a higher discharge will be allowed to more quickly bring the room to temperature.