(OP)
From ASCE 7-05 it appears that stack rooms have to be designed for a min LL of 150 psf. Is that all I need to use or should I be superimposing some other loads (partitions etc). 150 psf seems sort of light, so I wanted to make sure I get it right.

Thanks.

RE: Library stack room LL

There are a bunch of requirements for 150 psf - do you know the stack layout yet?  Don't forget there's also the 1000 lbs concentrated load.  If in doubt, try going for Heavy Storage at 250 psf.

RE: Library stack room LL

ASCE give miminum loads. If you feel that it is light, by all means increase it.
I think that their number takes into account the spaces between the shelves, but why lose any sleep over it? Make it 200 or 250 psf.  

RE: Library stack room LL

(OP)
@slta: Yes, I have the layout and its a typical stack 90" high by 1' deep (wide). Rows are going to be separated by 42" minimum.

JC, DST: thanks for the input. Looking at the link you posted, running some numbers based on 48 pcf paper density and also reading at this article I found via google: http://www.ce.udel.edu/courses/CIEG407/CIEG_407_Protected/Chapter%204%20Commentary.pdf

I have decided to use 180 psf LL as min.

RE: Library stack room LL

You might also want to give a little thought to stabilizing the stacks against overturning, particularly if they are in a seismically active zone.  One stack tipping over can start a domino effect.

BA

RE: Library stack room LL

Stacks of books are really heavy, I would recommend 250 PSF unreducible live load.

RE: Library stack room LL

(OP)
BA, we are in low seismic area, seismic design cat B per IBC 09. But its an interesting thought, how to stabilize against racking. I guess you would have to tie the stacks to the floor and each other!!
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources