I work at a packaging industry; we use blowers to suck the extra cuttings left at rotary die or printing. Recently we installed VFD at the blower motor.
Motor is 11KW; 3ph; the VFD is Toshiba VF-AS1 series.
I have adjusted the VFD at automatic torque boost and motor is running at 5KW at full speed i.e base frequency.
NOW the catch is that the Blower Duct Design and the motor selection is completely miscalculation. The motor is quite a lot bigger than the load. Is their any way to operate the same motor at rated frequency but less torque so the motor can be more energy efficient, or the selection i have made is the max this VFD can do.
Motor is 11KW; 3ph; the VFD is Toshiba VF-AS1 series.
I have adjusted the VFD at automatic torque boost and motor is running at 5KW at full speed i.e base frequency.
NOW the catch is that the Blower Duct Design and the motor selection is completely miscalculation. The motor is quite a lot bigger than the load. Is their any way to operate the same motor at rated frequency but less torque so the motor can be more energy efficient, or the selection i have made is the max this VFD can do.





RE: Best Parameter setting for VFD
RE: Best Parameter setting for VFD
iop995
The estimated output mechanical power according to the mathematical model fed in the VFD is about 4kW.
Now this means that the system is at about 80% efficiency at the moment.SO I think it is safe to predict possible 10-15% increase in efficiency after the equipment changing.
RE: Best Parameter setting for VFD
If the flow through the system is too great, then reduce the speed via the VFD. That is what is determining the motor loading.
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: Best Parameter setting for VFD
So let me explain again i am talking about full load when damper is fully open. I was actually asking that is it possible to use the VFD to improve the efficiency of the same over sized motor through some parameter adjustments as motors tend to become less efficient in under load conditions.
Phaphara
RE: Best Parameter setting for VFD
RE: Best Parameter setting for VFD
Changing the motor is not an easy fix. The wrong 5kW motor will be less efficient at 100% than the 11kW motor is at 50% load.
You could try reducing the motor voltage setting in the VFD. That might save some power. However, it will likely just make up for the extra losses introduced by the VFD.
At the end of the day, a VFD is an energy waster for a motor running at 100% speed. It's not rocket science. A contactor is 99.9999% efficient and a VFD is <95% efficient.
RE: Best Parameter setting for VFD
In theory, a small improvement in motor efficiency can be obtained by reducing the voltage (which reduces core losses and might reduce copper losses very slightly) while keeping speed constant, similar to the NOLA. Whether the amount of motor losses saved even matches the vfd losses is still a question.
=====================================
(2B)+(2B)' ?
RE: Best Parameter setting for VFD
Clarifcation:
Should have been
=====================================
(2B)+(2B)' ?