Free air space - code requirements
I was hoping soemeone could point me in the direction of where in ASHRAE does it dictate free air space requirment calculations. I ran the calcs for CFM but the client wishes to install a passive system. So the CFM calc means nothing, right?
CFM = Volume *3/60 (3ACH/60min/hr) = 80CFM
RE: Free air space - code requirements
What is free air space, or, rather, what do you mean by it?
He is probably thinking about natural air circulation which can also be expressed in CFM.
She - and yes, I am speaking of a passive/ natural air system. When I size my intake and exhaust louvers for a passive system it only uses free air specs so I need to calculate my req free area based on the ASHRAE code.
For example, on a residential crawlspace you have to meet a min req free air vent. You also have to meet these requirements in the attic area.
Does anyone know where I would look for these requirements.
Natural Ventilation is discussed in the ASHRAE Handbook, Fundamentals Volume, Chapter 16.
I believe that old UBC's addressed this requirement, and I'm sure the current IBC or ASCE7 do too.
Mike McCann
MMC Engineering
http://mmcengineering.tripod.com
Do you mean the free, or effective area of the louvre?  A natural vent calculation will provide the size of an open hole.  When you put a grille in the hole, it blocks a given amount of the space.  Any grille/louvre manufacturer will provide the free area of the grille product expressed as a percentage.