Check valve for vacuum relief
Does anyone have experience using check valves as vacuum breakers?
I need to provide a vacuum relief valve for an ASME Sec VIII pressure vessel (MAWP 30 psig) storing aqueous ammonia. I'm familiar with the API 2000 conservation vents from Groth, Protect-o-seal, Tyco, etc. but cannot use them for vacuum relief because I'm told these valves are not designed to withstand operating pressures above API 2000 ranges.
I have found VRVs that would work, but are not ideal due to their lead times or because they're not listed in my preferred manufacturer specifications.
I have read that a check valve can be used to provide vacuum relief and want to explore this option. I envision a valve with low cracking pressure mounted vertically (open end down).
Does anyone have experience with something like this?
RE: Check valve for vacuum relief
Good luck,
Latexman
a) What is the set pressure?
b) What is the rated capacity?
c) Can you periodically test the device?
d) What is the reliability? - will it work when it should work
If the consequence of damage is low or you can tolerate a broad range of vacuum -- then maybe a check valve could be ok.
Otherwise a calibrated device with periodic testing is indicated.
The bottom line is that there's nothing that says you can't use a check valve to protect pressure vessels from vacuum. If you do, that valve needs to be regularly inspected and tested, just like other pressure relief devices. Personally, I would want to have other layers of defense too. For example, I would want to have an ESD that shuts off the source of vacuum. that's especially true if the volume is high - you didn't mention how much ammonia we're talking about. If this is a very small vessel, then I'd consider just using the check valve. If it's a leage vessel, then I'd want additional layers of protection.
There is a prominent division between the low and high pressure tanks and relief valves. Conservation vents can't be used in my application as they are only designed for use on low pressure/atmospheric tanks and thus can't be exposed to the back pressures on a code vessel.
Finding a pressure relief valve for an ASME Sec VIII tank was of course easy, but not so for vacuum relief. Perhaps this is because pressure vessels are not susceptible to vacuum as you eluded to Don. Regardless, I was instructed to provide vacuum relief for this application.
Chance's questions proved difficult to answer. They made me realize that my issue was less about functionality and more about liability of using something not specifically designed for the application.
Fortunately I have now found a spring operated vacuum relief valve acceptable for use on ASME Sec VIII vessels that can withstand back pressures above my MAWP. It meets my other criteria (lead times, reputable manufacturer, etc.) so I believe it to be acceptable solution to my problem. Thank you to all who took time to share your thoughts.
Can you share more info on the valve you found? Make and model? I sometimes get involved in similar applications and am interested in what you found.