ETAP - Protection Time-Current Curves - Current offset error

ETAP - Protection Time-Current Curves - Current offset error

ETAP - Protection Time-Current Curves - Current offset error

(OP)
When I assign a fuse or relay from the ETAP library to the one-line diagram symbol of an existing ETAP model, ETAP  plots the time-current curve offset to the right by a current factor of 1.17.
When I assign the same fuse or  relay from the ETAP library to the one-line diagram in a new ETAP model, ETAP correctly plots the time-current curve without the current offset.

Have any ETAP users encountered this problem, and how is it resolved ?

 

RE: ETAP - Protection Time-Current Curves - Current offset error

I suspect there is an option set on the existing model to offset the curve to account for the difference in fault current seen in the phase overcurrent devices when there is a phase-phase fault on the wye side of a delta-wye transformer.  It is necessary to shift either the low side curve or the high curve to check selectivity for these faults.  

I don't know much about ETAP, but the 1.17 is suspiciously close to the actual factor of 1.15 to make me think it is probably related to this.

 

RE: ETAP - Protection Time-Current Curves - Current offset error

(OP)
Thanks dpc, the sqrt(3) / 2   pri/sec current ratio for a PP fault on the secondary of a delta/star transformer is accomodated in ETAP by the user applying a "shift factor" in "plot options".
However the "shift factor" is set to 1.00
I have found that by deleting the fuse or relay and re-assigning the  identical fuse or relay, the software plots correctly without the shift.  This not a satisfactory solution.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources