Equipment nameplate
Equipment nameplate
Hello. I need to come up with a nameplate for equipment we built and it has to state amps and full-load amps. It's a 3-phase, 208 VAC machine that has a 1/2 hp motor (1.8 Amps as per motor nameplate) and a few DC power supplies. How do I go about calculating these values? Do I add the 1.8 amps from the motor and the power supplies ratings?. Which would be the amps and which the full-load amps? Thanks for your help.
RE: Equipment nameplate
voltage but the inverter input D.C. 1.8 A it seems to be the rated current at rated voltage[ 208 V].
Bill
"Why not the best?"
Jimmy Carter