if i provide just minimum rebar for a 5ft - 32x32in pedestal, do i still need to satisfy the ties every other bar or less than 6"?
say i provide 12 bars. do i need ties in between?

RE: pedestal ties

I have wondered this and asked this question many times and came to the conclusion that they were needed, if for no other reason than 7.10.5.1 requires it.
The ties make construction easier usually anyway.

RE: pedestal ties

A pedestal is just a column - a short one at that - but you have to provide ties the same as a "regular" column the way I read ACI.

 

RE: pedestal ties

(OP)
can ACI 14.3.6 be applicable in this case?

RE: pedestal ties

I don't think section ACI 14.3.6 applies in my opinion -- I wouldn't consider a pedestal a wall...

However, I'd say you can likely design it as "Plain Concrete" per Section 22.8.  In this case you would not need tie bars, but you also could not consider the contribution of your vertical steel.

RE: pedestal ties

If this pedestal is poured monolithically with a wall, see 10.8.2 for some additional guidance.  While it doesn't specificaly address the quantity of ties, you may be able to use some judgement to eliminate the need for ties.

RE: pedestal ties

Can you provide 8 bars and use 2 ties or 1 tie + 2 crossties? Also, you can use the actual concrete area for strength as opposed to 32x32.

RE: pedestal ties

@delagina - Your second post - Can ACI section 14.3.6 be used? ACI defines wall as a member used to enclose or separate spaces. ACI does not give definition of a column based on the ratio of the cross-sectional dimensions. We have typically used UL Fire Resistance Directory classification, namely, cross-sectional ratio greater than 4 to distingush a wall from a column for design purposes.
For lightly loaded pedestals, not part of LLRS, and not in a high seismic zone, we only use outer ties at 12" o.c. We don't provide cross ties etc. However, we do show 3 ties at 4" o.c. at top of the pedestal.
Some time back I had posted a similar thread507-312673: Criterion for classifying a beam-column into flexural and compression. I did not get much of a response.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources