Undervoltage blocking of frequency relay

Undervoltage blocking of frequency relay

Undervoltage blocking of frequency relay

(OP)
Hi All,

Any ideas why to use undervoltage blocking for frequency functions (except the obvious one that below approx. 10% of Vnominal the accuracy may not be satisfactory)?
I heared some people wanting to set undervoltage blocking to 30% Vnom - are there any reasons to do that? Will these settings be different between different makes of PTs?

Thanks.

RE: Undervoltage blocking of frequency relay

It's just to avoid nuisance tripping on frequency when the voltage or voltage signal is not reliable, such as during faults, or issues with the PTs circuits.  30% is pretty typical, but the exact setting is not critical.

If you actually have 30% voltage on your system, the frequency is not going to be your main problem.  

RE: Undervoltage blocking of frequency relay

If you look at how the relay determines frequency it will better help you understand why.

The relay uses a clock to count the time between zero-crossings. During a fault, the DC offset of the voltage will shift the zero crossings, which is why you want a delay. After the breaker opens there can be ringing of the remaining voltage, which is why you want a high enough voltage cutoff.

If you want to look at each type of distribution PT, and capactance of each possible remaining system configuration, you can. We just use a level high enough that we don't need to do all the extra analysis.

RE: Undervoltage blocking of frequency relay

Depend on the frequency protection functionality.
1. Load Shedding
2. Generator protection.
3. Loss of main

usually between 0.3-0.6Un

RE: Undervoltage blocking of frequency relay

(OP)
Thanks for all your responses.

RE: Undervoltage blocking of frequency relay

(OP)
One more question :)

When talking about undervoltage - do you mean undervoltage on any phase or all three phases?

RE: Undervoltage blocking of frequency relay

The phase the under frequency is relay is on. It should be built into the under frequecny relay.

RE: Undervoltage blocking of frequency relay

(OP)
Not quite sure I understand - with multifunctional IEDs you normally have all three voltages connected and the phase selection algorithm for frequency measurement is internal to the IED, so you never know which phase is the relay actually looking at.
Am I missing something?

RE: Undervoltage blocking of frequency relay

I think, a last 25 years, under voltage release is part of under frequency relay. That means, it's operated on the same measurement circuit. In the digital relays, under voltage release is part of under frequency setting.  

RE: Undervoltage blocking of frequency relay

Under-voltage may be a good thing if the frequency draws down as a result of loading rather than a fault. Allowing or causing the voltage to drop with the frequency aids in recovery. Underfrequency may cause saturation in transformers and motors. Dropping the voltage to maintain the Volts per Hertz ratio may allow a recovery rather than experiencing an outage.
I would consider implementing under-voltage blocking during under-frequency events on islanded systems, small diesel systems and distributed generation plants that may become islanded.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Undervoltage blocking of frequency relay

If the manual dosen't say which phase frequency measurement is on then you should pester the manufacture for an answer.

In SEL the under voltage is part of the frequency settings, and dosen't matter.

RE: Undervoltage blocking of frequency relay

You usually do not need to worry about selecting a specific phase to protect with frequency settings and an undervoltage block.  Most often all three phases will see a freq change and the under voltage block is usually set as a phase to ground value. The undervoltage block will be active on whichever phase needs it, even if that is all three phases at once.    

RE: Undervoltage blocking of frequency relay

artvandelayb4u - (Side comment) Would a phase to ground measurment require wye-wye VT's?   

RE: Undervoltage blocking of frequency relay

You can measure frequency phase to phase.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources