I am analyzing a structure with vertical columns made from (2) w10x33 stacked on top of each other.
They are skip welded at the flanges and bolted through the flanges.
They are desinged to be one solid structrual member.
In my model I linked them with rigid links straight across ever foot or so.
When I run my model with a wind load the results I get are one of the pinned footings is in compression and the other is in tension.
I believe these are in reality acting as one member, so both should be in tension or compression.
Each of the columns are anchored in a pinned connection.
I started to put rigid links trussed diagonally from connection point to connection point but I am afraid this will make the column appear to be much much stronger than it is.
Any feedback would be greatly appreciated.
They are skip welded at the flanges and bolted through the flanges.
They are desinged to be one solid structrual member.
In my model I linked them with rigid links straight across ever foot or so.
When I run my model with a wind load the results I get are one of the pinned footings is in compression and the other is in tension.
I believe these are in reality acting as one member, so both should be in tension or compression.
Each of the columns are anchored in a pinned connection.
I started to put rigid links trussed diagonally from connection point to connection point but I am afraid this will make the column appear to be much much stronger than it is.
Any feedback would be greatly appreciated.





RE: Compound beams using rigid links
I would recommend one of two things:
1) Instead of using the rigid links, model this as a single member with the A, I and J of the built-up section. Then the force results for that member correspond to the design forces for the built up member. It's much easier to interpret your results in that case.
2) Continue what you have done. But, at the bottom of the column (where you have the boundary condition) replace the two boundary conditions with a single boundary at the centroid of the built-up cross section. This boundary condition will be connected via links to the two column members. That way, you only have one reaction result to worry about.
RE: Compound beams using rigid links
Thanks for the reply.
I think I will go with one connection at the centroid of the two members.
They are supported together at one pier, so it seems to me that one anchor point is more realistic.
Also I am done with the model, and that will be the easiest fix ;) .