Are there tap rules on medium voltage circuits?
Are there tap rules on medium voltage circuits?
(OP)
We are planning to install a new 1200 Amp switchgear that will be fed from some open overhead outdoor aluminum busbar. The bus bar is rated at 3000 Amps and 15kV. We are tapping (2) 500 kcmil/phase, MV-105, 133%EPR insulated cables from the busbar to the new switchgear. The switchgear is about 100'away. Are there any rules on medium voltage when tapping like this we need to observe?






RE: Are there tap rules on medium voltage circuits?
RE: Are there tap rules on medium voltage circuits?
Alan
RE: Are there tap rules on medium voltage circuits?
But, anyway, the insulated cable shall be provided with suitable termination in order to avoid moisture ingress and leakage .