Grounding transformer placement

Grounding transformer placement

Grounding transformer placement

(OP)
Project consists of a 3-phase 95kW solar PV plant connected to a 12.47kV distribution line.  The 480V inverter's isolation transformer is connected delta-wye with high-resistance grounding.

PV setup:
http://i1245.photobucket.com/albums/gg581/jchebahtah/inverter.png

simplified single-line:
http://i1245.photobucket.com/albums/gg581/jchebahtah/singleline.png

It was determined that a grounding transformer is needed to prevent possible overvoltages during a ground fault (if feeder breaker opens and PV remains in-service forming an island).

Any preference of where to install the grounding transformer (480V or 12.47kV level)?

It would certainly be cheaper to throw the xfmr on the 480V...

Justin Chebahtah
www.justinchebahtah.com

RE: Grounding transformer placement

If the wye-wye transformer is solidly grounded on both sides it should be possible to achieve an effectively grounded system on the high side using a grounding transformer on the low side.  If either side of the wye-wye is not solidly grounded the grounding transformer must be on the high side to become effectively grounded.

RE: Grounding transformer placement

(OP)
Thank you very much for the prompt, concise, and informative response. Enjoy the star!  

Justin Chebahtah
www.justinchebahtah.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources