We have the following situation:

1500 kVA delta delta transformer with a 240V secondary 3ph 3W connected to a 5000A 240V bus.  We are then feeding a 500 kVA autotransformer (wye connected; 480V secondary) to an automatic transfer switch (3ph 3W).  Our customer purchased a 450 kW 480V wye connected generator for a backup generator connected to the ATS.  My question is how do I ground the generator?

RE: Connecting wye generator to a 480V delta system

How is your delta system grounded? It will ground the generator if it is direct connected. There may be protection issues.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Connecting wye generator to a 480V delta system

(OP)
The delta system is ungrounded, there is an equipment ground available for bonding at the main service.

RE: Connecting wye generator to a 480V delta system

You may float the neutral at the generator. Any grounding method applied to the generator will be applied to the system when on generator power. I would consider high impedance grounding. Also consider high impedance grounding the system and carrying that ground through to the generator.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources