Errata HI ANSI 9.8
Errata HI ANSI 9.8
Hi All,
Has anyone any knowledge of there being an error in the formula in this standard (9.8.7.3)?
The formula given is S = 1.0D + 2.3(Q/0.785*D^2)/(g*D)^0.5)*D
where Q is in L/s;D in metres;g 9.81m/s
For Q=750 L/s D= 1m I get 702m which is incredibly high?
"Sharing knowledge is the way to immortality"
His Holiness the Dalai Lama.
http://waterhammer.hopout.com.au/
RE: Errata HI ANSI 9.8
If you enter your data in the formula reported in HI ANSI 9.8 but for imperial units:
S = 1.0*D + 2.3((12*0,409*Q/D^2)/(12*g*D)^0.5)*D
with:
S in inches
D in inches
Q in USgpm
g = 32,3 ft/s^2
you'll get S = 67 inch = 1.7 m (which is what you'd get entering Q in m^3/s in the formula for metric system
Thanks for that. I wonder if ANSI/HI know? The second formula in 9.8.7.3 works with Q in L/s.
The second formula on the other hand works with Q in l/s, because if you take a look at it you'll notice that the term 1/1069 at denominator is given by:
2.3/(785*(9,81)^0.5)
While in the first formula they've reported 0.785, which clearly exhibits a shift of a 10^3 factor (from l/s to m^3/s).
Said that I sincerely don't know whether at the HI are aware of this.
