Condensation above false ceiling

Condensation above false ceiling

Condensation above false ceiling

(OP)
We have air conditioned a car showroom, having 2" thick sandwich panel roofing. Below the sandwich panel, there is sloping false ceiling, made of aluminum tiles  insulated with 10 mm thick closed cell rubber insulation with aluminum facing. The average height between the roof and the false ceiling is about 80 cm. The supply ducting is through a gypsum bulk head below the false ceiling and the return is also taken direct to the AC unit, below the false ceiling. The room design is at 23 deg C DB, 50% RH and the design ambient is 46 deg C DB, 29.44 deg C WB.

We are worried about the possibility of condensation above the false ceiling, especially during the peak summer. Can somebody suggest any solution?

Regards,

gmcshj

 

RE: Condensation above false ceiling

I can't appreciate why you might be overly concerned about condensation, based on your posting.  The supply and return is happening below the false ceiling, if anything the false ceiling space will be warm.

Other than that: Don't direct supply air onto the alloy faced false ceiling and minimize infiltration.

 

RE: Condensation above false ceiling

The problem is you have two layers insulation and the condition of the air between the two layers is undefined. If the gap has air infiltration from the outside it may cause condensation. So you must prevent outside air infiltration and allow some inside air infiltration (ventilation) of the gap. This will slightly reduce total thermal insulation but but does not negate the value of the inner layer of insulation.

RE: Condensation above false ceiling

Keep the building slightly positive to avoid infiltration, an air/vapour barrier building wrap would be helpful.   

RE: Condensation above false ceiling

I am trying to figure out what kind of suggestion are you looking for.

If you are designing, you can calculate duct insulation using higher relative humidity figures.

If that is built already, the best you could do is to open false ceiling space so that some level of natural ventilation occurs there, as humidity will be highest in space which is tight bu not resistant to vapor mass transfer.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources