Propane Tank Sizing
Propane Tank Sizing
I am trying to size a above ground liquid propane tank for use with an emergency generator.
I calculate required run times, convert from natural gas cfh to propane cfh, calculate wetted area of the tank based on % full, design temperature of the day, but what I am having trouble with is frost generation due to relative humidity.
I haven't found much engineering literature about doing this. The engineering books (and some propane literature) I have found say to consider frost. From them, for a 0 F design day, the usable temperature difference could vary from 2 F to 29 F, depending on the relative humidity
But the literature from the generator manufacturer, the engineering staff for the generator, and even an engineer for a large propane supplier do not seem to take frost into consideration.
I don't want to tell the equipment engineers who have been doing this a lot longer than I have that they are wrong, but I cannot discount that much of a variance in other engineering literature.
Has anybody designed these and am I missing something?
RE: Propane Tank Sizing
The generator we have specified would be running on propane vapor.
Steve
Looking at the following information is what got me thinking there is more to it than temperature.
www.doc
The approach advised by Emerson would make it a very large tank. The math works, but it is one of those instances where actual experience is lacking to tell me that my numbers are suspect.