Smart questions
Smart answers
Smart people
Join Eng-Tips Forums
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login




Remember Me
Forgot Password?
Join Us!

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.
Jobs from Indeed

Link To This Forum!

Partner Button
Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

magoo2 (Electrical) (OP)
6 Feb 12 18:20
Can someone describe the zero sequence impedance of an inverter?  I've heard it described as a delta winding in a transformer, so it is just an open circuit.  So if I have a generator or photovoltaic array behind it, it doesn't matter since the open circuit is there for the inverter.

Can someone validate this assumption.  Thanks.  
davidbeach (Electrical)
6 Feb 12 19:47
Inverter as in power electronics, or inverter as in packaged UL-1741 compliant assembly complete with isolation transformer?
magoo2 (Electrical) (OP)
6 Feb 12 20:11
UL-1741 compliant inverters.
davidbeach (Electrical)
6 Feb 12 20:50
Zero sequence impedance of the "inverter" will be essentially indistinguishable from the zero sequence impedance of the isolation transformer.
magoo2 (Electrical) (OP)
7 Feb 12 8:51
I'm not sure exactly what you're saying.

If I have a delta grd-wye isolation transformer, then I get a break or open in the zero sequence.  So I get no contribution from the inverter for a single line to ground fault on the primary or secondary of the stepup transformer.  Is that what you're getting at?
Helpful Member!  davidbeach (Electrical)
7 Feb 12 9:34
The UL-1741 packaged "inverter" (assuming 3-phase) all most certainly contains an isolation transformer that is delta on the power electronics side and grounded wye on the system side.  This is necessary to meet the IEEE-1547 requirement to be compatible with the utility grounding system.  As such, the isolation transformer functions as a ground source just as any other grounded wye-delta transformer would.  The zero sequence impedance of the "inverter" is just the zero sequence impedance of the transformer and the power electronics are open circuited in the zero sequence (probably connected in delta anyway).
magoo2 (Electrical) (OP)
7 Feb 12 13:09
Many thanks, David.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Back To Forum

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close