Firmware Update for GE Fanuc Series 90 Micro
thread791-126480: Firmware woes for new plc user - help please
After days trying to update the PLC firmware I decided create this post to save others people time as I could not find a complete solution in forums. I hope will be useful...
=>Firmware Update for GE Fanuc Series 90 Micro via USB to RS422 Adapter (IC690USB901) utilizing Windows 7
- Download Series 90 Micro firmware release 3.10 at GE Automation Support web site http://support.ge-ip.com
You must register for free to get a SSO login and password. (I had to e-mail them because I could not register at the first time as I did not have a customer number)
- Extract the files and copy it to a USB Drive strait to the prompt (outside any folder).
- Download and install DoxBox at http://www.dosbox.com it is an MS-Dos emulator for windows that works much better them the windows cmd opening software for 32bits systems.
- Install the cable drivers, in my experience I had my USB Adaptor set automatically as COM5; as the GE firmware update utility just has just 2 options of ports (COM1 & COM2) we have to change it at:
Control Panel>Device Manager>Ports
At Port Settings Tab click in Advanced to set the USB adaptor port as COM1 or COM2
Also the Port Settings must be set as 19200bps; Data bits: 8; Parity: Odd; Stop bits: 1; Flow control: None
- Open the DOSBox
At the Z:> prompt:
Configure the serial port typing
serialX=directserial realport:comX (X must be 1 or 2 as you set in the Windows Port Settings)
Mount the USB Drive and run the firmware update utility typing:
mount A G:/ (where G is your USB Drive Letter)
Z:>cd A:
A:>install
Following the instructions in the installation document that come with the update utility you must have the PLC stoped;
Inside the firmware update utility press F3 to set the Port pressing TAB and ENTER to confirm
Press F1 to attach to the PLC and F1 again to Boot and Install the new firmware
After finishing the firmware update the installation utility will tell you to restart the PLC.
Done!
- Open the DOSBox
At the Z:> prompt:
Z:>cd A:
A:>install
Done!