Patterson Rig #491 Boiler Explosion

Patterson Rig #491 Boiler Explosion

Patterson Rig #491 Boiler Explosion

(OP)
Matthew Lawson posted this on the AWS forum and I would like to share this important information to all operators, inspectors and construction personnel in general.

"January 28th, 2012

Drilling Ahead has received a report that Patterson Rig #491  drilling at Keene, North Dakota near Williston  had a boiler explode last night killing one and seriously injuring another.

The deceased worker identified to us only as "Rickey" was a married 38-year-old who had just broke out in August of 2011. The worker who pulled Rickey away from the exploded boiler is in the hospital with third degree burns."

Read more:  http://www.drillingahead.com/page/patterson-uti-rig-491-boiler-explodes-killing-worker-injuring-ano?xgs=1&xg_source=msg_share_page#ixzz1lC2Ss5Rd
  

RE: Patterson Rig #491 Boiler Explosion

The safety of boilers depends on the statutes/laws of the location where the boiler operates.

Is this really an issue about a boiler being dragged from state-to-state with no real regulatory oversight ?

What are the rules in North Dakota regarding the use, safety and operation of temporary boilers ?

Or is it a case of unqualified operators jury rigging the LWCs ?

Boilers in some states require a 24/7 operator, other states....no

   

RE: Patterson Rig #491 Boiler Explosion

Looking at the link, the boiler is a typical fire tube of the Scotch-marine type.  Historically, these boilers have good safety history.  The cause of the explosion can be one of several reasons such as overpressure coupled with malfunctioning safety valves; low water condition resulting in overheating the tubes and furnace and when discovered, cold water was immediately introduced; fuel oil seeping into the water side and coating tubes and furnaces; and last and not least sabotage of the safety controls and equipment.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources