Short Circuit calculations with site rated gas turbines

Short Circuit calculations with site rated gas turbines

Short Circuit calculations with site rated gas turbines

(OP)
I am working with a gas turbine gen set and I have some questions regarding Short Circuit calculations and Short Circuit power.

The turbine has a site rating of about 12,5 MW (15,6 MVA) and a ISO rating of about 15 MW (18,5 MVA) power factor of 0.8. The alternator is rated 18,5 MVA.

So when I calculate the SC rating I use the alternator name plate rating of 18,5MVA.

My question is, will you always get maximum SC current independent of the turbine output? Or do I have to have ideal circumstances where the turbine gives the needed mechanical power?

If the current is dependent on the mechanical power from the turbine, can you detail?
 

RE: Short Circuit calculations with site rated gas turbines

A short circuit takes a lot of MVA but little MW.
Power equals current times voltage times power factor.
In the event of a short circuit the voltage may be very low so the power or MW requirements are lowered.
The short circuit current is very reactive so although there are a lot of KVAs, when that is multiplied by the low power factor resulting from the reactive current  the KW or MW demands are lowered.
I would use the alternator rating for short circuit calcs.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Short Circuit calculations with site rated gas turbines

The short circuit behaviour is principally controlled by the transient and sub-transient reactances of the alternator,and are almost completely independent of the prime mover over the duration of the fault.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources