Due to a some interesting existing conditions, I have been asked to attach a beam to an existing pilaster in a way that results in torsion on the connection.  We will be drilling and epoxying anchors into the pilaster and they will be loaded with eccentricity in the plane of the connection.  I have analyzed this condition using the Elastc method for eccentrically loaded bolt groups per AISC.  My question is whether the brittle nature of concrete violates the assumptions of this method.  In other words, will the worst-case bolts take all the load and fail (bond failure or concrete bearing) before the other bolts see the load due to insufficient deformations.  Any thoughts??

RE: eccentrucally loaded bolt group in concrete

(OP)
Thaks Connect.  I have never used Profis, but I will check it out.

 

RE: eccentrucally loaded bolt group in concrete

(OP)
Profis seems to assume a force distribution similar to that of the Elastic Method mentioned preiously.

As I was checking my calculations though, I noted that Profis uses a very low Spacing Adjustment factor (fA) compared to values I have used in the past.  For HY 150 epoxy w/ 5/8" Dia HAS, the fA value used by Profis is 0.343 for a 3" anchor spacing.  From my understanding of the HILTI manual, fA should never be less than 0.70 for HY 150 and comes to around 0.73 for this condition.  I am not very familiar with the program and I may be missing some input, but something does not seem correct here.  Has anyone had much experience with design using Profis?

RE: eccentrucally loaded bolt group in concrete

I don't see any issue using the elastic method in your case.

RE: eccentrucally loaded bolt group in concrete

I have done the elastic method as you are describing in the past. I dont see a problem with it either. One thing to note:  I'm assuming you aren't in a seismic area a HY150 is not cracked concrete approved.  

RE: eccentrucally loaded bolt group in concrete

(OP)
Thanks for the responses.

The seismic category is borderline (SDC B with Site Class C, SDC C with Site Class D), so I am fighting on whether to go with HY150 or a seismic approved epoxy (RE500 SD).  

The ironic thing is that the existing structure that we are working on (only adding RTU's) is all un-reinforced masonry built in the mid 80's.  Not exactly seismic friendly...

RE: eccentrucally loaded bolt group in concrete

Hilti make HIT-HY 150 MAX-SD, which is cracked concrete approved.

ESR-3013

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources