I trying to find an example of how to design a interior non-loading bearing cmu wall for out of plane seismic loading. Does anyone know of such example
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Non-load bearing cmu wall design
|
RE: Non-load bearing cmu wall design
RE: Non-load bearing cmu wall design
the wall is 16' tall
RE: Non-load bearing cmu wall design
How does an interior wall get hit by 90 mph wind??
RE: Non-load bearing cmu wall design
I'd distribute the seismic as a uniform pressure and design the wall on a 1-foot basis. Size the reinforcing as you would for any other lateral load on a wall (similiar to cantilevered beam).