Heat exchanger vacuum breaker?

Heat exchanger vacuum breaker?

Heat exchanger vacuum breaker?

(OP)
I have been told to add a vacuum breaker to our exchanger to prevent condensate build up during times of low inlet steam flow. From what I have seen a vacuum breaker works by allowing atmosphere in during situations when the pressure in the exchanger is less than atmospheric. My question is, won't allowing atmosphere in allow corrosive Co2 and O2 into the steam?

RE: Heat exchanger vacuum breaker?

From my view point, install a VB into exchanger has not sense. Because inlet of atmospheric air would cause more condensation for steam.

Regards

RE: Heat exchanger vacuum breaker?

Have to say that I have never heard that one before. I agree with you 100%.

RE: Heat exchanger vacuum breaker?

The recommendation is correct, but the reasoning is wrong.  Installing a vacuum breaker and/or air vent to the shell side of steam to liquid heat exchangers is always recommended by every major (and minor) manufacturer.  

The vacuum breaker/vent should be used in accordance with the type of steam system you've got.  The reason is to prevent steam hammer that may occur if residual condensate remains at the bottom of the shell after the steam regulating valve has closed.

THe reason to include it is not for when there is low demand, but when there is NO demand, and steam is not flowing.  The breaker/vent helps prevent steam hammer (and damage to the tube bundle) from occurring when demand resumes, and the steam valve re-opens.  If you have other measures in place to completely remove condensate from the shell of the heat exchanger when the steam valve is closed, then a vacuum breaker/air vent are not necessary.

-TJ Orlowski

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources