catch basin design

catch basin design

(OP)
i need help please. i need to know if there is a sprecific design procedure for sizing catch pits/catch basins to get the appropriate dimmensions.thanks.

RE: catch basin design

Design Criteria should be set by your local agency.  If they do not have criteria identified then you can default to the lext level up similar to this:

City
County
State
Federal

RE: catch basin design

Your local DNR might be helpful or the county officials as noted above.

RE: catch basin design

(OP)
The CATCHPIT/BASIN I HAVE IS DRAINING FROM LAND E.G PARK LAND NOT FRM ROAD SIDE KERBS/CUBRS. IF I HAVE THE FLOW HW DO I SIZE THE CATCHPIT. ALSO THIS CATCHPIT IS LINKED TO AN UNDERGROUND STORMWATER PIPE NETWORK ALREADY. see attached standard detail to get the idea.

RE: catch basin design

first size the inlet to capture the flow
second set basin v depth to account for inlet loss into the storm drain. you will need the hgl of the storm drian main pipe

if the inlet is grated, make sure to account for clogging
 

RE: catch basin design

Download the link I gave you above.

Read it.  Take your time and understand it.  You can skip the stuff about gutter flow and gutter spread for this particular question, but not the stuff about the grates.  

Find your grate in the link, or the closest approximate.

Consider it a 'sag inlet.'  

Assume a clogging ratio that is conservative for your application.  

Calculate the head over the grate necessary to push the flow through the grate.  Make a note of this head.  

Now calculate the HGL in the pipe network, using modified rational method or something similar.  Make a note of that elevation.

Compare the two.  The depth of the "catch pit" as you say must be large enough to handle the worst of those two conditions.

 

Hydrology, Drainage Analysis, Flood Studies, and Complex Stormwater Litigation for Atlanta and the South East - http://www.campbellcivil.com

RE: catch basin design

beej67: Nice link and explanation.

Also don't forget to contact the manufacturer for the minimum depths of the devices.

B+W Engineering and Design
Los Angeles Civil and Structural Engineering
http://bwengr.com

RE: catch basin design

(OP)
thank you very much guys

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources